Re: Atwood Furnace
It is always a good idea to work the electrical plugs on & off several times as the first step in any electrical issue, especially with 12V control circuits. In the case of any DSI heating device (furnace or water heater) the voltage that is returned to the igniter circuit board to indicate that the flame is burning is only measured in microvolts. If you happen to have a dirty connection, especially common with edge connectors such as most RV boards use, that voltage could very easily be lost. I suspect that the thing that fixed your problem was most likely the action of removing the connector and then putting it back.
It might be well worth your time to clean the contacts on that connector when you have a chance. A good way to do this is by using a typing eraser to clean them and carefully blow out all of the residue from the cleaning. Last, wipe it down with a good quality isopropyl alcohol.